Gas Issue

This category is for discussing a wide range of topics including hot water, cold water, heaters, black & grey holding tanks etc.
User avatar
Kappy
Posts: 410
Joined: Mon Feb 29, 2016 11:24 am
Location: Wagin WA

Re: Gas Issue

Post by Kappy »

Interestingly just went out and observed spark etc.

Well there is spark and gas and the gas ignites till the clicking stopped and goes out.

The system seems to only attempt ignition twice and then I have to go and re set swith inside bus. However on doing the the damn thing ignited and stayed on. Doh Doh.

Then when turning off and restarting again, back to the same deal gas flow , ignites and then goes out when clicking stops,.......scratches head.
Cheers

Kappy

Growing older is inevitable, growing up is optional.
User avatar
Jon and Kay
Posts: 728
Joined: Tue Dec 04, 2012 5:08 pm

Re: Gas Issue

Post by Jon and Kay »

Sensor needs adjusting to be closer to flame.
Jon
User avatar
Busman
Posts: 1261
Joined: Wed Dec 05, 2012 10:09 pm
Location: Stanthorpe QLD
Has thanked: 1 time
Been thanked: 2 times

Re: Gas Issue

Post by Busman »

Yups
Vanishing Point, almost ready to vanish
Suzuki GV more than ready to go NOW !
Hans
Posts: 15
Joined: Wed Dec 05, 2012 4:30 pm
Location: Ballajura WA

Re: Gas Issue

Post by Hans »

Hi, from memory when I had my gas HWS installed, it is a Rinnai Infinity 16, the gas regulator had to be of a larger capacity, 250 Mj/hr, standard Marshall regulators are 150 Mj/hr. Copper piping had to be 3/4 inch. Is it worth a check that the gas supply to your HW unit is sufficient to keep to the unit running after initial start up. Check the gas consumption of your HWS, is the Regulator and/or copper piping of sufficient size? Regards, Hans
User avatar
Kappy
Posts: 410
Joined: Mon Feb 29, 2016 11:24 am
Location: Wagin WA

Re: Gas Issue

Post by Kappy »

Hans wrote:Hi, from memory when I had my gas HWS installed, it is a Rinnai Infinity 16, the gas regulator had to be of a larger capacity, 250 Mj/hr, standard Marshall regulators are 150 Mj/hr. Copper piping had to be 3/4 inch. Is it worth a check that the gas supply to your HW unit is sufficient to keep to the unit running after initial start up. Check the gas consumption of your HWS, is the Regulator and/or copper piping of sufficient size? Regards, Hans
Thanks this is a Suburban HWS that was working ok for some time.

I changed the regulator as a precaution and will have to check Mj rate.

I don't even know how one adjusts the sensor, so I would appreciate some guidance on that.

Cheers
Kappy
Cheers

Kappy

Growing older is inevitable, growing up is optional.
User avatar
BruceS
Site Admin
Posts: 9304
Joined: Thu Nov 22, 2012 7:32 pm
Location: Mannum, SA, 5238
Has thanked: 36 times
Been thanked: 36 times

Re: Gas Issue

Post by BruceS »

There is a little 'probe' about half inch long that sits in the pilot flame. As long as the pilot flame is aimed at the probe & it gets hot, the gas will keep flowing. It is so that if a gust of wind (Chuck?) blows out the pilot, the gas will stop flowing.
That tin tunnel that the flame goes through might need a cleanout too? I had spider webs in mine some time ago plus some rust flakes or something. I took it off, gave a good clean out & no more problems.
*******************
BruceS
Mannum, SA

********************
User avatar
Kappy
Posts: 410
Joined: Mon Feb 29, 2016 11:24 am
Location: Wagin WA

Re: Gas Issue

Post by Kappy »

BruceS wrote:There is a little 'probe' about half inch long that sits in the pilot flame. As long as the pilot flame is aimed at the probe & it gets hot, the gas will keep flowing. It is so that if a gust of wind (Chuck?) blows out the pilot, the gas will stop flowing.
That tin tunnel that the flame goes through might need a cleanout too? I had spider webs in mine some time ago plus some rust flakes or something. I took it off, gave a good clean out & no more problems.

Thanks Bruce I will check it out.

Cheers
Kappy
Cheers

Kappy

Growing older is inevitable, growing up is optional.
User avatar
Kappy
Posts: 410
Joined: Mon Feb 29, 2016 11:24 am
Location: Wagin WA

Re: Gas Issue

Post by Kappy »

Hi
Been away for a bit, had a flying visit to the Gold Coast.

I'm really confused with this damn hot water system, I have managed to get it running but it still is intermittent.

I have cleaned the tube couldn't see any debris in there.

Mainly I see the gas ignite but as soon as the spark stops the burning gas goes out, I have no idea where the pilot light is or if there is even one.

seriously considering sacking this @%%%&^^** suburban heater and getting a rinnai infinity, I had one installed on a house I once owned, worked great and efficient. I doubt id these Suburban heaters are really efficient yes or no, anyone

Has anyone fitted a rinnai or have any knowledge.

In the interim can someone lead me to any troubleshooting with pics haha.
DSC_0554 (1024x576) (800x450).jpg
You do not have the required permissions to view the files attached to this post.
Cheers

Kappy

Growing older is inevitable, growing up is optional.
User avatar
Jon and Kay
Posts: 728
Joined: Tue Dec 04, 2012 5:08 pm

Re: Gas Issue

Post by Jon and Kay »

That looks like the old SW10 , it has a sensor on the control board, instead of a thermocouple. You would need to have the board removed and the flame sensor checked, or replace with a new board. Dinosaur Electronics (USA) make a good replacement board said to be better than the original, which appears to have this common problem. OR a new instant water heater as you have suggested.
Jon
User avatar
Busman
Posts: 1261
Joined: Wed Dec 05, 2012 10:09 pm
Location: Stanthorpe QLD
Has thanked: 1 time
Been thanked: 2 times

Re: Gas Issue

Post by Busman »

Hans has fitted one, look at earlier posts this thread
Vanishing Point, almost ready to vanish
Suzuki GV more than ready to go NOW !