Hi Dapopedapope wrote:Peter, how often would you repaste then?
As I said that was with a Utilux product & was over 25 years ago that they were redone
I retired shortly after we redid them ,So do not know how they went the 2nd time

My message is simply do not wait for 20years check regularly
Fairly easy to do with a sensitve multi meter[one that will read micro volts]
Take readings NOW with cell under a known load that you can repeat
Measure between the actual cells' terminal and the connections as close as possible to the cell terminal & between connection & conection
They should ALL be VERY close to the same reading
That will give you an indication of a clean new setup
Record readings [even on the connectors] then say do 1st check after 6months
if no significany change repeat yearly !!
PeterQ