Can you check the surge current supplied by the inverter, on air con start up
The inverter digital read out will be too slow,I believe', but you could give it a try, really a job for a fast analogue amp meter

It could be that the RVD's MCBO is tripping simply on the Surge current, not the RVD on a voltage leak
What is the claimed surge current capacity of the inverter?[4000W]
The inverter it self does not temporarily shut down& then reset??? for just a minute or so??
Did a quick search but cannot find much in the way of a manual

I think Ian would be more interested in having a happy customer ,who is in a position to support the product

Try your luck

ps at the week end help son finish his grid tie solar installation, new meter installed ,now on line but had some interesting problems of the unit tripping out due to over voltage
I have mentioned in another place about our consistently high mains voltage[254V]
This,combined with line impedance,lead to the inverter seeing a line voltage in excess of 265V [the safety shut down point]
Just had Energex out,they reduced the mains voltage to 240V but cannot go any lower due to need to maintain voltage at the end of the line
Still having the occasional shut down when the sun is bright
Going to put in some oversized cables between inverter a mains input to switchboard to gain some points of a volt[expect about [0.5V]
But it seems the problem is more in the street mains, & the number of solar set ups in the area all feeding back
Peter