Lithium batteries online

Post by Newcastle George »

Terry,

How do the specs look on this LiFePO4 battery https://outbax.com.au/voltax-12v-135ah- ... g-rv-solar? I would need two in series for 24V. I would be replacing the 4 x 6V 260Ah lead acids currently in use.

George
George, Julie, Leonie & Sean - Kotara, Newcastle
DIY 11.5M 1979 Bedford, Nissan/UD FE6T motor
User avatar
supersparky
Posts: 8786
Joined: Mon Nov 26, 2012 7:00 pm
Location: Home on the beautiful Gold Coast for a while.
Has thanked: 81 times
Been thanked: 66 times

Re: Lithium batteries online

Post by supersparky »

George, If you are looking to go lithium, why you get
T1 Lithium to make you a 24v battery to suit your needs.
Cheers
David

David and Terrie
2006 Winnebago Alpine
Not all who wander are lost.
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Lithium batteries online

Post by T1 Terry »

Newcastle George wrote: Fri Nov 13, 2020 8:33 am Terry,

How do the specs look on this LiFePO4 battery https://outbax.com.au/voltax-12v-135ah- ... g-rv-solar? I would need two in series for 24V. I would be replacing the 4 x 6V 260Ah lead acids currently in use.

George
A lot of the specs are misleading down to out right furphies,
1) LiFeP04 chemistry can not operate below 0*C, only the LYP chemistry can do that and only Winston Chung holds the patent for that chemistry. The electrolyte properties can be altered to move the operating range lower, but the upper operating range reduces by the same amount.
2) Charge an LiFeP04 battery to 14.6v would push the cell voltage to 3.65v ... if you could be sure the cells were perfectly balanced at the very top end of the charging. Their specified charge rate is 30 amps to 50 amps, no balancer can transfer 50 amps from the high cell to the low cell to stop the high cell voltage from running away and destroying itself.
3) just like you can't have light weight lead, you can't have light weight LiFeP04 chemistry cells. A genuine 100Ah @ 12v LiFeP04 battery weighs around 15kg to 16kg, so there is no way you could get 135Ah out of a 12.6kg battery .... unless you do tricky discharge rates like 1 amp rather than the 50% of the capacity load rate that is supposed to be the standard for testing lithium batteries.
4) The discharge cut off is 10v, 2.5v per cell if again, it was perfectly balanced. The trick is, you can not top balance (fully charged) and bottom balance (fully discharged) at the same time, the battery is managed at either one end or the other, it can't be both ends of the range. This would require perfectly matched capacity and internal resistance cells, NASA stuff, not off the shelf $660 stuff, more like $100,000 batteries .....
Then, you only get a 2,000 cycle life? As Dottie would say WTF??? If you can't get 5,000 cycle out of a lithium battery it is because it is built out of poor quality stuff ... or the whole battery management system is poor causing an early death of the cells ......

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
User avatar
Newcastle George
Posts: 3284
Joined: Wed Dec 05, 2012 3:21 pm
Location: Kotara, Newcastle
Has thanked: 2 times
Been thanked: 8 times

Re: Lithium batteries online

Post by Newcastle George »

Thanks Terry, I had my doubts.

Could you get Margaret to give me a rough quote for approx 150Ah 24V T1 Lithium setup? I have a PL60 controller, 1kW of solar and a Victron BMV 702.

George
George, Julie, Leonie & Sean - Kotara, Newcastle
DIY 11.5M 1979 Bedford, Nissan/UD FE6T motor
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Lithium batteries online

Post by T1 Terry »

Newcastle George wrote: Fri Nov 13, 2020 11:13 am Thanks Terry, I had my doubts.

Could you get Margaret to give me a rough quote for approx 150Ah 24V T1 Lithium setup? I have a PL60 controller, 1kW of solar and a Victron BMV 702.

George
Best to contact Margaret direct on the phone or via email. If you Google T1 Lithium the web site will come up with the phone number and the email contact addresses. Margaret can ask you direct the relevant questions. 100Ah or 160Ah or 200Ah or multiples of any one of those capacities, those are the cell capacities we carry, anything else would be special order.

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Lithium batteries online

Post by T1 Terry »

I was watching one of the Will Prowse test videos https://www.youtube.com/watch?v=RxMIs0PXrBw and he was testing one of these batteries https://www.sokbattery.com/12v-200ah-li ... -pack.html The test load he uses is not the correct test load for an LiFeP04 battery, but advertised as 206Ah it would really be around the 150Ah mark you mentioned and they claim a 3,000 to 8,000 cycle life so more like what would be expected.
They also mention they can be connected in series to get the 24v you are looking for and because you only want a small capacity battery, the cost of a full T1 lithium BMS might push the total battery cost over the top for you. Up to you, just thought I'd mention it.
Note: These batteries can not be used in parallel, so you can't build a bigger capacity battery by linking them in parallel to increase the capacity to what you need and I doubt they could supply a high draw inverter that would be required to power a microwave or air conditioner etc, not even a kettle and Will didn't seem keen to put the hot air gun right up to the 2000w full load so ..... a lithium battery that can be charged relatively quickly but not suitable for high discharge loads. A 200Ah LYP battery built by us would be able to supply 600 amps @ 12v for 20 mins or until the cell voltage dropped to the point the BMS disconnected the battery, that is a long way from the 40 amp or less load Will was willing to test the battery at ... I know, bad pun :roll:

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
Mrcoolabah1au
Posts: 2699
Joined: Wed Jan 23, 2013 3:36 pm
Location: Tocumwal on the Murray river

Re: Lithium batteries online

Post by Mrcoolabah1au »

We got T1 to put in 200ah the first time around 👍
Coolabah1au
Wayne nini
native pepper
Posts: 1357
Joined: Mon Feb 23, 2015 8:21 am
Location: Tasmania
Has thanked: 5 times
Been thanked: 4 times

Re: Lithium batteries online

Post by native pepper »

T1 Terry wrote: Fri Nov 13, 2020 1:46 pm Note: These batteries can not be used in parallel, T1 Terry
Terry could you explain why these batteries can't be used in parallel, I have an idea why, but an explanation would be great help to many looking to go down the path of lifepo4 I feel so they can avoid the scams. Unless it is so technical you need a degree to understand it :?

My feelings with regard to the charge parameters manufacturers are providing, is to create redundancy after a few years, I note most give less than 10 year warranty, when they should be giving 20 years with proper charge parameters.
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Lithium batteries online

Post by T1 Terry »

native pepper wrote: Fri Nov 13, 2020 3:03 pm
T1 Terry wrote: Fri Nov 13, 2020 1:46 pm Note: These batteries can not be used in parallel, T1 Terry
Terry could you explain why these batteries can't be used in parallel, I have an idea why, but an explanation would be great help to many looking to go down the path of lifepo4 I feel so they can avoid the scams. Unless it is so technical you need a degree to understand it :?

My feelings with regard to the charge parameters manufacturers are providing, is to create redundancy after a few years, I note most give less than 10 year warranty, when they should be giving 20 years with proper charge parameters.
Here goes :lol: As a starting point, I'll explain why a battery becomes unserviceable (can't be fixed and won't do the job required)
All batteries die at the single cell level, it is only one bad cell in an AGM or any lead acid battery that makes it no longer operational. All big batteries are built with the single cell terminals available so the voltage can be measured to see if each cell is within its safe operating zone. If the single poor performing cell can be brought back into a serviceable state or replaced if it can not be recovered, the whole battery can be returned to service rather than junked.
A single cell dies because:
1) it has either a low level or run out of electrolyte and this damages the plate surface
2) It has been excessively discharged to zero volts and the higher voltage from the other cells forces current through the 0 voltage cell actually reversing the current flow .....this destroys any chemical cell, but is an absolute death sentence to a lithium chemistry cell.
3) The cell is charged beyond full capacity causing the voltage to rise excessively and closely followed by a serious over heat, boiling the electrolyte away and buckling the plates or (in the case of lithium cells) causing them to build up metal transferred from one plate to the other eventually bridging the gap between the plates creating a short circuit within that cell.
To avoid cell damage, the cell voltage should be monitored and maintained within the same operating voltages, look after the cell voltages and the battery voltage will look after itself (yeah, I stole that from the pennies and pounds line)

The drop in batteries have very small current shunts for balancing each cell and small cabling and contactor or just single contact relays or mosfet transistors to control the battery isolation if the battery voltage goes too high or too low. They rely on all the cells remaining perfectly in balance and just measure the total battery voltage, not the individual cell voltages so any cell can go over voltage or under voltage (even within the same battery pack) yet the total voltage of all the cells remains within the 10vdc to 14.6vdc range that so many of the drop in lithium batteries use for their BMS shut down. A few minutes with a pen and paper and you will see how many combinations of 4 numbers will still add up to either 10vdc or 14.6vdc. Any number outside the 2.8vdc and 3.6vdc is a cell being damaged, any over 4vdc is a cell being murdered, the same for under 1.5vdc. If any cell goes to 4.5vdc or 0vdc, that cell is irreparably damaged or dead.

Time for a coffee and possibly a re-read to get all this sorted, or time to go and look some where interesting :lol:

OK, for those still with us, why can't the 12v batteries be paralleled. All lithium batteries have very low internal resistance, this means the battery with the shortest cable length to the load or the charging point, will do all the work until that battery can't do it any more without the voltage going high or low (at the terminals, not just at the cells) then the next battery with a slightly long cable length takes over the job and so on down the line.

Now think about the small cable size and current carrying ability of the battery isolation used that I mentioned before. To power a 2400w appliance (standard 10 amp power point plug and lead is anywhere up to 2400w, maybe a bit more sometimes) the inverter needs an extra 10% to do the conversion from DC to ripple free AC @ 230vdc allowing for the losses to heat as well (cause nothing ever works perfectly, there are always losses) the battery needs to supply 2640w.
Watts = amps x volts, divide 2640w by 12v at the battery = 205 amps. To carry 200 amps without the resistance causing so much heat the wire burns and the voltage drops so low the inverter shuts down, you need heavy sized battery cable even for a short run of a mtr or so, even bigger if the cable length is longer. We are talking cable the thickness of the average male middle finger ..... can you imagine that size cable being used inside a drop in battery? Not likely is it. Next, to disconnect the battery at 200 amps @ 12v, contact faces about the diameter of the widest part of the average males thumb are required and one at each end of the contactor bar to ensure the circuit is broken and there isn't just a big arc forming and burning the faces of the contact. This size contactor in the Gigavac range is around the $300 to $350 range and around the size of an open hand, heal to finger tip ..... can you imagine them spending that much money and having room for that in a drop in battery ..... unless you are paying around $1500 each for them.

There is no method of power sharing that sort of current in any drop in battery, the size required would be substantial, the heat generated would be substantial so couldn't be installed inside a sealed case, the sophisticated electrics required would be more than the price of the battery ....

All this just to product enough power to boil the kettle or power the microwave, what about running the air conditioner and other appliances at the same time, so a 3,000w or bigger inverter .....

Those in the "know" on those other forums told us it couldn't be done, but we have been doing it for more than 10yrs and the batteries are still performing fine so .......

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Lithium batteries online

Post by T1 Terry »

Brucie2 wrote: Sat Nov 14, 2020 3:06 pm Oh Boy!!
Terry do you know who that *&@$# on the cruiser forum is?
Hellia44?
https://www.cruisersforum.com/forums/f1 ... 42369.html
He didn't respond to me!!
:lol: I bet he doesn't like the reply I left for him :lol:

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows